EWC Controls Forum

Discuss your HVAC issues here.
It is currently Sun May 19, 2013 10:31 pm

All times are UTC - 5 hours [ DST ]




Post new topic Reply to topic  [ 2 posts ] 
Author Message
 Post subject: Emergency Heat
PostPosted: Sat Dec 11, 2010 10:15 am 
Offline

Joined: Tue Nov 30, 2010 11:39 pm
Posts: 4
Is the Emergency Heat/ Normal switch, available on a terminal block? I want to provide a convent switch for the customer to access. (not in the attic)

The system is using a UZC4 setup with a two stage Heat Pump condenser ,dual fuel two stage emergency heat(Gas) and Digital thermostats (2 Cool,4 Heat) with humidity sensors, OAS, RAS, SAS installed. I have eight wires to each thermostat. All of the wires are in use. (R C Y1 Y2 W1 W2 G DHum)

I know if I had one more wire for "O" then I could change the UZC4 and the thermostats to HP, and allow the thermostat to call for emergency heat. Is the Emergency Heat/ Normal switch, available on a terminal block any where?


Top
 Profile  
 
 Post subject: Re: Emergency Heat
PostPosted: Mon Dec 13, 2010 4:50 pm 
Unfortunately, there is no terminal for the Emergency Heat Switch.

If you switch to Heatpump thermostats you can abandon the 'G' terminal and use the wire for the Reversing valve. The panel will operate Heating and Cooling demands normally with out the G present, you will only lose the ability to call for Fan Only.

Eric


Top
  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
Powered by phpBB® Forum Software © phpBB Group