I have a Ruud Oil Furnace with a NCM300 Panel and 2 zones.
This was installed 5 years ago and never had an issue until lately.

Not always but often the zones stop calling for heat yet the furnace itself, fan too, does not shut down.
This has required a power-off of the whole system, on re-energizing the system seems to work correctly, but then within a couple of days it does it again.

The oil service company doesn't have a clue, I would like to know if the panel is going goofy and needs to be replaced.

Thanks,


Top
 Profile  
 
PostPosted: Thu Jan 19, 2012 12:07 pm 
Offline

Joined: Fri Mar 13, 2009 11:12 am
Posts: 148
Jeff,

When the thermostat is satisfied but the furnace continues to run, what lights are lit on the NCM-300 zone panel?
This information will be key in determining what is causing this problem.

_________________
Patrick Cyrana
Pcyrana@ewccontrols.com
1-800-446-3110


Top
 Profile  
 
PostPosted: Thu Jan 19, 2012 12:16 pm 
Offline

Joined: Thu Jan 19, 2012 10:58 am
Posts: 3
The next time it does this I will get back to you guys.

It may be a couple of days to check, since I had to reset the system this AM.

I spoke to Bob, I think, and he told me the same thing and how to check it all.
For the record the Ver is 1.2 on the chip.

I'll get back to you.

Thank you.


Top
 Profile  
 
PostPosted: Wed Jan 25, 2012 10:47 am 
Offline

Joined: Thu Jan 19, 2012 10:58 am
Posts: 3
Hi Guys,

OK here is the scoop.
When the thermostats are satisfied the LEDs on the NCM300 are #1 (system) flashing and #3-5 (Zone Dampers 1-3) steady on.
#7 (fault) is not on as are no others.

With a reset of the furnace itself, the burner power switch not the circuit breaker, the system resets and then goes back to normal operation, for a while only.
Did not power off the NCM300.

During normal ops, the zone 1 LED (calling in winter) is off.
The issue is getting worse, as I have had to reset it now 4 times since last night 11pm.

Not sure if it is the fan master control relay down low or the master stack control up by the burner.
I'm leaning towards the master stack control (Honeywell box w/ reset switch).

What's your thoughts?


Top
 Profile  
 
PostPosted: Tue Jan 31, 2012 5:22 pm 
Offline

Joined: Fri Mar 13, 2009 11:12 am
Posts: 148
Jeff
I apologize for taking so long to get back to you.
Due to the nature of your situation I would suggest you call our Tech Support Hotline at 1-800 446 3110.
We are available Monday through Friday from 8am to 5pm.
There are several questions that need to be answered before I can draw any conclusions, so to expedite that process I suggest calling as soon as possible.
Thanks

_________________
Patrick Cyrana
Pcyrana@ewccontrols.com
1-800-446-3110


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 5 posts ] 

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group