NCM300 - Maximum URD and SID Dampers
NCM300 - Maximum URD and SID Dampers
What is the maximum number of URD and/or SID dampers that can be connect to one zone of the NCM300 before you need to use an auxiliary relay with an additional transformer?
-
Eric K.
Re: NCM300 - Maximum URD and SID Dampers
A maximum of 12 per zone and 25 total across all zones. The largest transformer you can use is a 24vac 60VA transformer.
Eric
Eric
Re: NCM300 - Maximum URD and SID Dampers
Wow. The NCM300 can actually handle enough current to control up to 12 URD or SID dampers on one zone. I have to assume then that the URD and SID dampers must have very low current drive motors.
I'll have 10 dampers on two zones for a total of 20 dampers in the system and I'll use a 24Vac 60AV transformer.
Thanks.
I'll have 10 dampers on two zones for a total of 20 dampers in the system and I'll use a 24Vac 60AV transformer.
Thanks.