I have an EWC-ST-2D Control connected to 2 zones. Zone 2 has two SMD/MAN actuators (I believe this is the correct model. Blue case with terminals 1-6 & X, Z) and one of these seems to be functioning erratically. At times it will be closed when the furnace is on and the other actuator is open and vice versa. Is there a way to test it to see if its functioning properly? Is it possible for the open/close to be reversed somehow on one actuator?

Thanks for any info


Top
 Profile  
 
PostPosted: Mon Dec 05, 2011 4:37 pm 
Offline

Joined: Fri Mar 13, 2009 11:12 am
Posts: 148
To test an MAN motor you
- apply voltage 24VAC to terminals 1 and 4; with voltage on terminals 1 and 4 only the motor should move to the Open position.
- apply voltage 24VAC to terminals 1 and 6; with voltage on terminals 1 and 6 only the motor should move to the Closed position.

If you do not have wires on the 2 and 5 terminals that run back to the zone panel then you will need a jumper on each individual motor across the 2 and 5 terminals.

It is possible but very unlikely that the open and closed would be reversed on that motor.
Why? Do you think you think that is what is occurring?

_________________
Patrick Cyrana
Pcyrana@ewccontrols.com
1-800-446-3110


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group